DW98

Member
There are two buildings each with a service. One building has a generator, and we would like to back-up some equipment in the other building. Is this permissible? What code articles cover this? 225? 230?
 

DW98

Member
Owner wants to install branch circuits from the building with generator to the other building to back up telephone equipment.
 

north star

Senior Member
Location
inside Area 51
= & =

From the `08 NEC, Article 445.19: "A single generator supplying more than
one load, or multiple generators operating in parallel, shall be permitted to
supply either of the following:
(1) A vertical switchboard with separate
sections, or
(2) Individual enclosures with overcurrent protection tapped
from a single feeder for load separation and distribution."

= & =
 

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
There are two buildings each with a service. One building has a generator, and we would like to back-up some equipment in the other building. Is this permissible? What code articles cover this? 225? 230?
Take a look at 225.30(a)(4).
 