catveeguy

New member
I am having a disagreement with my counterparts in other states on bonding armored fiber at power verticals. I believe they should be bonded, and my counterparts say they only need to be bonded at the enclosures. We could be miles between enclosures, and I do believe that that causes a differance in potential at all poles between those enclosures. I look forward to the response. Thank you. catveeguy
 

LEO2854

Esteemed Member
Location
Ma
I am having a disagreement with my counterparts in other states on bonding armored fiber at power verticals. I believe they should be bonded, and my counterparts say they only need to be bonded at the enclosures. We could be miles between enclosures, and I do believe that that causes a differance in potential at all poles between those enclosures. I look forward to the response. Thank you. catveeguy

I'm not 100% sure,But This may be what you are looking for.

Welcome to the forum..:thumbsup:


IV. Grounding Methods
840.100 ONT and Optical Fiber Cable Grounding.

Grounding required for protection of the ONT and optical
fiber cable shall comply with 770.100, 800.100, or 820.100,
as applicable.
 