infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Straight, bends doesn't matter.

(C) Stranded Conductors. Where installed in raceways,
conductors 8 AWG and larger, not specifically permitted or
required elsewhere in this Code to be solid, shall be
stranded.
 

jumper

Senior Member
310.3 Stranded Conductors. Where installed in raceways,
conductors of size 8 AWG and larger shall be stranded.

Exception: As permitted or required elsewhere in this
Code.

Rob got it, I type way too slow again.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
When you mentioned the #3 solid I wondered where in the world you would find that animal. I would be almost as surprised if you found a THHN that did not also have a THWN rating, but, to answer, a "W" conductor is needed both due to the exposure at the weatherhead and being inside an outdoor raceway. (THWN, RHW, XHHW, etc)