Junction box sizing

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
314.28.

A junction box has a 3" straight pull left to right, and a 2" angle pull from left to bottom.

How tall does the box have to be? I think 15", the answer key says 12".
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I think the answer key is incorrect.

12" is distance between the conduit not the size of the box.

Minimum size of the box is 15" by 24"
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I think the answer key is incorrect.

12" is distance between the conduit not the size of the box.

Minimum size of the box is 15" by 24"

The box is 24" long so the distance between the two angle pull conduits could be at least 20", so how did you calculate to get 15"?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would tend to agree with the book since the straight pull really has no affect on the height. The problem as I see it is whether that straight pull should come into play with the angle pull and IMO it should not but by the wording in the NEC it appears to come in-- I am not sure that is the intent.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I will add this graphic but I am not sure if you are using Mike Holt books or not

ry%3D480
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
The box is 24" long so the distance between the two angle pull conduits could be at least 20", so how did you calculate to get 15"?

Could be at least 20" or Has to be at least 20". Are you thinking what the premade boxes are sized to?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
2" x 6 = 12 between the angle pull raceways.

(2" x 6) + 3" = 15" for the height of the box.

The 2" and 3" enclose different conductors.

This is the part I'm missing. The box is already 24" long (straight pull) so couldn't the angle pull conduits already be separated by at least 20"?
 