Would NEC permit the Underground generator room (separate building)?
I've seen in supplier's catalogs but our client has some fears and recommends to check NFPA.
The issue is our architect doesn't want to affect the building facade. So the underground solution is the most likely here.IMHO...
Look at 701.12
unless its Optional....
The issue is our architect doesn't want to affect the building facade. So the underground solution is the most likely here.
Anyway, I've read twice 701.12...Are you sure it's there?!!:slaphead:
Yes, but the client has another concerns regarding the emission of SOX and NOX where the exhaust will be in grade level...Is it real issue?:?Flooding concerns can ususally be dealt with by pumps.
In my area, tornado's and high winds would be more of a concern than a flood. i rarely get the chance, but I would usually prefer to put generators below grade for that reason.
Yes, but the client has another concerns regarding the emission of SOX and NOX where the exhaust will be in grade level...Is it real issue?:?
Again building facade...hhhhit only runs when the power is out. if it is a big problem run an exhaust pipe up in the air as far as is necessary to alleviate his concerns.
The EPA may well require a stack and diffuser at a certain height.
Typically we have put them in the basements of buildings with the mechanical contractor handing the exhaust out of the building.
Again building facade...hhhh