The contractor mounted the means of disconnect for VAV boxes to the ceiling grid. The disconnect is just a simple toggle switch with pilot light. Was wondering if this is an acceptable means of mounting? I can't seem to find anything in the code saying that it can't be mounted here. The VAV box is located just above the switch in question, approx. 24". The switch is mounted to a junction box that has the straps spanning the grid T-Bar similar to a smoke detector installation.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
The contractor mounted the means of disconnect for VAV boxes to the ceiling grid. The disconnect is just a simple toggle switch with pilot light. Was wondering if this is an acceptable means of mounting? I can't seem to find anything in the code saying that it can't be mounted here. The VAV box is located just above the switch in question, approx. 24". The switch is mounted to a junction box that has the straps spanning the grid T-Bar similar to a smoke detector installation.
300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place. Support wires that do not provide secure support shall not be permitted as the sole support. Support wires and associated fittings that provide secure support and that are installed in addition to the ceiling grid support wires shall be permitted as the sole support. Where independent support wires are used, they shall be secured at both ends. Cables and raceways shall not be supported by ceiling grids.
 
Status
Not open for further replies.
Top