We have contractors currently installing a UPS. The wire size for the primary input of the UPS is 3 #2/0 + 1 #6 ground in 2" rigid conduit (per drawing). The wire type is XHHW-2. When the UPS arrived it had a 200-amp circuit breaker instead of 175-amp. Do we need to upgrade the wire size to 3/0? The terminations in the UPS are NOT labeled and listed for 90 degrees, therefore I believe the 75 degree C rating on Table 310-16 must be used.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The over-current device ahead of your conductors would be the protection for the conductors. If you protect your 2/0s at 175 amps and they feed the UPS breaker it makes no difference what size that (UPS) breaker is.
 

etinkham

Member
Location
DC, MD , VA
More info

More info

I need to make clarifications. The UPS breaker is 200-amp. The contractor cannot get a 175 amp breaker for the old switchgear and they are going to install a 200-amp breaker. The wire size is 2/0. The Engineer is claiming the 2/0 wire size is okay based on the current rating on the 90 degree scale on 310-16 for XHHW-2 wire. The terminations in the UPS and the new breaker going in the switchgear are not labeled and identified for 90 degree terminations. I believe the wire size must be based on the 75 degree scale on 310-16 which is 3/0 for 200-amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I need to make clarifications. The UPS breaker is 200-amp. The contractor cannot get a 175 amp breaker for the old switchgear and they are going to install a 200-amp breaker. The wire size is 2/0. The Engineer is claiming the 2/0 wire size is okay based on the current rating on the 90 degree scale on 310-16 for XHHW-2 wire. The terminations in the UPS and the new breaker going in the switchgear are not labeled and identified for 90 degree terminations. I believe the wire size must be based on the 75 degree scale on 310-16 which is 3/0 for 200-amps.

I would disagree with the engineer.
 

Volta

Senior Member
Location
Columbus, Ohio
... The terminations in the UPS and the new breaker going in the switchgear are not labeled and identified for 90 degree terminations. I believe the wire size must be based on the 75 degree scale on 310-16 which is 3/0 for 200-amps.


I agree. They cannot upsize the protection under 240.4(B) either as 175 is a standard size.
 