Corner grounded 480
Corner grounded 480
You have a corner grounded 480 volt system. Three wire delta. The grounded phase has zero volts to ground, the other two phases have 480 volts to ground. The utility will install a Form 12S meter, which is set up so that the 5th jaw is connected to B phase, so that is normally the one that is grounded. But in actuality, any phase labeling is meaningless as long as the grounded phase is connected to the horizontal 5th jaw of the meter socket. Downstream labeling should be consistent with the service entrance phasing.
As discussed in many previous posts, corner grounding 480 is a practice that has differing opinions as to its safety. In the industrial field I work in, which is a drinking water and electric utility, 480 delta is never grounded and is replaced with 277/480 Wye whenever finances permit. Reasons for grounding are that a ground fault will trip the breaker if either ungrounded phase faults to ground. But...in incedental contact between ground and an ungrounded phase is basically a phase to phase event. The drawback to an ungrounded system is that Code requires ground fault indication and if the system is not monitored, that fault can remain undetected. The upside is that an incidental contact will not be nearly as serious. As an electrician working around this stuff, I kinda hate both setups. 277/480 Wye is a better way to go, but more expensive due to the extra wire for the neutral. just my opinion.