I asked this question on the NEC forum and got 0 answers I was wondering if you could help
What I have is a metal heating grid system outside a container to melt zinc inside a large metal container (pot)
Current problem is 60 year old GE breaker that looks like switch gear does not open and close properly, old open close window flag gets stuck and one of the ct monitoring coils recently caught fire.
Also I am not sure it is set uo right to begin with so let me post some info
Plant power is 480V ungrounded delta
Feeds to transformer cuts down to 240v 2 wire
600 Breaker/OL feeds 1000KCM thhn wire in conduit to a metal grid no blowers
Breaker has mechanical adjustment wheel adjusted beyond 100% so it dont trip
By current coil measured current is approximately 590 amps.
I am not sure if this needs a breaker OL combo?
Does it requir some form of GFCI protection?
I am not sure if the wire is capable of this current?
Does 125% continuos load apply to wire size 590*125%=737amps? 1000kcm thhn 615amp
I am not sure of heating grid common practice I have been trying to make some sense out 427 I think our pot would be considered a vessel
What I have is a metal heating grid system outside a container to melt zinc inside a large metal container (pot)
Current problem is 60 year old GE breaker that looks like switch gear does not open and close properly, old open close window flag gets stuck and one of the ct monitoring coils recently caught fire.
Also I am not sure it is set uo right to begin with so let me post some info
Plant power is 480V ungrounded delta
Feeds to transformer cuts down to 240v 2 wire
600 Breaker/OL feeds 1000KCM thhn wire in conduit to a metal grid no blowers
Breaker has mechanical adjustment wheel adjusted beyond 100% so it dont trip
By current coil measured current is approximately 590 amps.
I am not sure if this needs a breaker OL combo?
Does it requir some form of GFCI protection?
I am not sure if the wire is capable of this current?
Does 125% continuos load apply to wire size 590*125%=737amps? 1000kcm thhn 615amp
I am not sure of heating grid common practice I have been trying to make some sense out 427 I think our pot would be considered a vessel