Only by de-energizing the equipment (making diagnostics difficult) or by temporarily removing whatever justified the classification in the first place.Hazardous location newbie question? if the equipment in the EP enclosure are not explosion proof also, how are repairs, diagnosis and maintenance safely and easily performed on the interior of the EP enclosure in a potentially explosive atmosphere?
I took it that he already had an enclosure rated class 1 div 2 with a PLC inside of it and was asking if he added relays inside the enclosure did they have to be hermetically sealed.
So I'll repeat mine too,
If you have an enclosure that is Class 1 Div 2 rated with the proper seals there is no need for hermetically sealed relays.
I'll humor you by saying I work in Class 1 Division 1 areas and most all of the enclosures are explosion proof with sealoffs for every entry with non-hermetically sealed devices inside if them. Engineers design.
Mostly just the light switches are hermetically sealed and dont require sealoffs.
3 of the 4 walls are 8" reinforced concrete and the outside wall is hinged so in case of an explosion the blast blows everything outside
instead of into the plant.