I understand the standard and optional service/feeder calculations for residential services, however, I am struggling to clearly understand how to attack the subpanel load calculations. I have several high end residential projects that I am currently involved in and this issue arises on every one of them. For example:
I can justify a 400 amp main service for the house using the service/feeder calculations, so I specify a 400A, 120/240V 1ph 3W meter/main assembly. These units can only accommodate up to two 200/2 subfeed breakers, so I specify two 200A, 120/240V 1ph 3W subpanels.
Then, when I assign individual branch circuits in the house to the two 200 amp subpanels I've chosen, the connected loads exceed the panel rating. I cannot justify a 200 amp panel that shows 230 amps of connected load. The local AHJ is requesting panel schedules and I don't believe they will approve such an installation.
Is there a diversity/demand calculation that can be applied to the subpanels as well? Please include code references, links, etc. that I can use. Thanks.
I can justify a 400 amp main service for the house using the service/feeder calculations, so I specify a 400A, 120/240V 1ph 3W meter/main assembly. These units can only accommodate up to two 200/2 subfeed breakers, so I specify two 200A, 120/240V 1ph 3W subpanels.
Then, when I assign individual branch circuits in the house to the two 200 amp subpanels I've chosen, the connected loads exceed the panel rating. I cannot justify a 200 amp panel that shows 230 amps of connected load. The local AHJ is requesting panel schedules and I don't believe they will approve such an installation.
Is there a diversity/demand calculation that can be applied to the subpanels as well? Please include code references, links, etc. that I can use. Thanks.