Where in the NEC does it say we can't use aluminum wiring for branch wiring smaller than #8 gauge.
Or do I need to look in the UL white book?
the n.e.c permits you to install 12/2 & 10/2 aluminum nm cable.
It did for a couple of years in the mid-70s, but as you said the damage was done by the failures of the older stuff and it never really got back any market share. The new alloy along with the CO/ALR devices did not have the issues of the older aluminum and standard wiring devices....
Back starting in about the mid 60's it was very common to see #12 and #10 AL wire. Problem was that the alloys used then were not what they are today and AL wiring got a bad rep. and justifyably so. The alloys of today are vastly improved but the damage was done and it never came back in the smaller sizes.
240.4(D) also specifically describes use of 12AWG Al with a 15 amp OCPD.It doesn't, see Table 310.15(B)(16) (formerly Table 310.16) for listed/approved sizes of AL conductors.
Although insurance companies may frown on this install.
550.15
Many times the restriction is in the state or local codes. For example, the New Mexico electrical code prohibits aluminum smaller than #8 unless used as an EGC.
See 250.64(A) for the restriction on aluminum within 18" of the earth. It only applies to Grounding Electrode Conductors. See 344.10(A)(3) for the aluminum conduit.did i hear right somewhere in mike holt's training that aluminum wire cannot be installed less than 18 inches from earth? i don't want to go thru 30 hours of video to hear 1 sentence if so how about aluminum conduit?
Only applies to "trailers". You can call them manufactured homes, mobile homes, or factory built homes, but a trailer by any other name is still a trailer.
"...shall be permitted to be installed where judged suitable for the environment" sounds like a bit of a copout to me.See 344.10(A)(3) for the aluminum conduit.
You have to read all of the section. That part does not apply to concrete encased or directly buried."...shall be permitted to be installed where judged suitable for the environment" sounds like a bit of a copout to me.
