People want to bring in new homes to our park with higher rated panels than the pedestal has, so they want to upgrade the pedestal. Here is an example.
We have 3 homes on a 150A distribution breaker. A developer wants to bring in a home with a 100A panel. NEC article 550-22 suggests that with 3 homes we can use a demand factor of 0.44 giving each home capacity for 113A. So the answer would be yes.
I spoke with our local Building Dept who said that the sum of the pedestal breakers should not exceed the rating on the distribution breaker. So the answer would be no.
Which one is right?
We have 3 homes on a 150A distribution breaker. A developer wants to bring in a home with a 100A panel. NEC article 550-22 suggests that with 3 homes we can use a demand factor of 0.44 giving each home capacity for 113A. So the answer would be yes.
I spoke with our local Building Dept who said that the sum of the pedestal breakers should not exceed the rating on the distribution breaker. So the answer would be no.
Which one is right?