Hello I'am an italian electrical engineer that work in the world of the cooling tower. In our site we have to realize a Lightning Protection System in accordance to NFPA 780.
I read the NFPA 780 (edition 2004) and in the section 4.2 Materials is written as shown below:
4.2 Protection systems shall be made of materials that are resistant to corrosion or protected against corrosion.
4.2.2 One or more of the materials in 4.2.2.1through 4.2.2.3shall be used.
4.2.2.1 Copper.Copper shall be of the grade required for commercial electrical work and shall be of 95 percent conductivity when annealed.
4.2.2.2 Copper Alloys.Copper alloy shall be as resistant to corrosion as copper.
4.2.2.3 Aluminum.
(A) Aluminum shall not be used where contact with the earth is possible or where rapid deterioration is
possible.
(B) Conductors shall be of electrical grade aluminum.
Now my question is:
As per NFPA 780 and yout experience, Can I use hot dip galvanized steel? Hot dip galvanized steel is in accordance with point 4.2 (Protection systems shall be made of materials that are resistant to corrosion or protected against corrosion)
If this is possible where I can find this infromation on the NFPA standard?
Thanks
Bye
4.2.2.3 Aluminum.
possible.
Now my question is:
Thanks
Bye