So this has come up on a job we have. The junction box at each light fixture is identified with panel, phase and circuit number, the wiring is the proper phasing (brown-orange-yellow-grey), but we used either 12-2 (black-white) or 12-3(black-red-white) mc cable from the junction box to the light fixture. The electrical inspector wants the mc to be re-identified at the light fixture to phase and circuit, even though the junction box which feeds the light fixture is right above the fixture. The job is under 2011 code, and all I am seeing is 210.5(C), but looking for a solution besides opening up every light fixture in the building.