How is the 4-20mA points determined for the 4mA (deg F) and the 20mA (deg F) values? Is there any standard or formula for determining the transmitter temperature span?

In my process I am using a thermocouple. My process temperature range is 60F to 110F.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
How is the 4-20mA points determined for the 4mA (deg F) and the 20mA (deg F) values? Is there any standard or formula for determining the transmitter temperature span?

In my process I am using a thermocouple. My process temperature range is 60F to 110F.

There is no "standard" as such.

Most times one would set the span of the xmtr so that

1) the actual expected temperatures including unusual conditions will always be within the span.

2) the "normal" reading will be perhaps 50-75% of full span.

It is not always possible to get #2 depending on #1.

I try to use something that is reasonably straightforward like 0-100 deg C. However, I have a customer who always uses strange spans on temp xmtrs like 20-220 deg F. No idea where he came up with that, although it is not far off from 0-100 deg C.
 

Dale Hayes

Senior Member
Part 2

Part 2

Another Question:

Some Temperature Transmitter vendors offer the output signal at (4 to 20)mA or (20 to 4)mA. What is the purpose of a 20-4mA?
 