I have a 1200 amp 3 phase 480 volt service MDP (WITH NO MAIN SWITCH)
They are using only (5) five fused switches in this panel.
The main lugs have space for (4) four 750 Kcmil wires and (3) three are used by the incoming feeders. (3) Three sets of 600?s
The next available over current device would be the 13,800 volt pole mounted transformer fusing.
The power company pole mounted transformers are (3) each; 100 KVA 1 phase units. The 13,800 volt fusing size is unknown but only protects this set of transformers.
Can I use the open lug on the MDP to make a feeder tap on the existing service with 350 Kcmil?
Is this discussed in the code? Where?