service riser "AWESOME"

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I saw this yesturday, what do you think. Please add any and all code sections that you think apply
 

Attachments

  • 2013-03-28_15-32-12_837.jpg
    2013-03-28_15-32-12_837.jpg
    141.6 KB · Views: 2

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Code sections don't apply to surreal art. :D


Roger
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I have heard, "looks like Jenga" and "looks like something the Cat in the Hat would do."
 

jap

Senior Member
Occupation
Electrician
Depending on the angle of the offsets, they may have broke the 360 degree rule, That and I dont think
any of it would be wrench tight since the threads would have never worked out that way.

JAP>
 

jap

Senior Member
Occupation
Electrician
Very Nice that they took the time to screw a 2" hub to the top of the panel instead of just settling for a
locknut :)and a bushing.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can you imagine that configuration having to carry a fault current :D
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I believe the couplings and the hub is listed for rigid conduit. Now, is the offset considered rigid, I don't know.
 