Or worse if the grounding path back to source were to ever open, everything connected to this ground will be at 120 volt potential and could get someone killed, Don't do it, and make sure those in charge of this guy know what he is doing and saying, one death from someone like this should never be allowed to happen.
The other danger even if the ground path doesn't open is, if there is a fault between the hot and neutral this fault current can be very high, the voltage drop of the grounding path can cause a high enough voltage to be present on the grounding paths that some one could be hurt or killed, so again never use an EGC for a current carrying conductor NEVER, and it is also very against code.