Does this appear to be correct? Im concerned about how to apply to large load I have for the driveway snow melt system.
Here is my optional load calculation. I'm including the (2) HVAC condensor units.
2,880w (ACCU 1)
3,360w (ACCU 2)
1,200w (AHU 1)
1,200w (AHU 2)
8,640w (total AC)
AC vs. Heat (oil furnace with hot water baseboard, AC's a much larger load)
54,676w (including driveway snow melt, nameplate of all appliances, 3w per sq ft, (2) small appliance ckt, laundry ckt)
Table 220-30
100% of the nameplate rating(s) of the air conditioning = 8,640 watts
100% of the first 10kVA of all other loads = 10,000 watts
40% of the remainder of all other loads = 17,870 watts
TOTAL OPTIONAL LOAD 36,510 watts
Article 220-2
TOTAL OPTIONAL LOAD 36,510 watts DIVIDED BY 240 VOLTS = 152.125 AMPS
Therefor a 200A single phase service would be okay to accommodate these loads.
Here is my optional load calculation. I'm including the (2) HVAC condensor units.
2,880w (ACCU 1)
3,360w (ACCU 2)
1,200w (AHU 1)
1,200w (AHU 2)
8,640w (total AC)
AC vs. Heat (oil furnace with hot water baseboard, AC's a much larger load)
54,676w (including driveway snow melt, nameplate of all appliances, 3w per sq ft, (2) small appliance ckt, laundry ckt)
Table 220-30
100% of the nameplate rating(s) of the air conditioning = 8,640 watts
100% of the first 10kVA of all other loads = 10,000 watts
40% of the remainder of all other loads = 17,870 watts
TOTAL OPTIONAL LOAD 36,510 watts
Article 220-2
TOTAL OPTIONAL LOAD 36,510 watts DIVIDED BY 240 VOLTS = 152.125 AMPS
Therefor a 200A single phase service would be okay to accommodate these loads.