Hall way receptacles

Status
Not open for further replies.

ToolHound

Senior Member
In a dwelling unit hall way is 22' do I need 1 or 2 receptacles?

Well, here's what the 2011 NEC Code sez:

Chapter 2 Wiring and Protection
ARTICLE 210 Branch Circuits
III. Required Outlets

210.52(H)
(H)
Hallways. In dwelling units, hallways of 3.0 m (10 ft) or more in length shall have at least one receptacle outlet.

As used in this subsection, the hallway length shall be considered the length along the centerline of the hallway without passing through a doorway.

My reading of this is...there is a requirement, and the requirement is a minimum of one receptacle outlet per hallway of 10 ft or more in length.

Seems like you need one recep outlet for 22 ft dwelling hallway.

-ToolHound
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Only one per code as long as there is no door way in between.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Only one per code as long as there is no door way in between.

When I first read your comment I pictured a door along the wall. If that is what you meant, then it is incorrect. If you meant a doorway breaking up the hallway in to two sections then I agree. I think that is why the code uses the exact words it does about passing through a doorway.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
When I first read your comment I pictured a door along the wall. If that is what you meant, then it is incorrect. If you meant a doorway breaking up the hallway in to two sections then I agree. I think that is why the code uses the exact words it does about passing through a doorway.

I guess you agree. :happyyes:

I meant a door way perpendicular to the hall way.
 