New Residential Service Sizing when the computation is very close to service size.

Status
Not open for further replies.

smclott

Member
After running the Optional Calculation for One Family Dwelling,,, I come up with a diversified, bottom line number of 47,720 volt-amps ,, at 240V that divides out to 198.83 amp service. Does that mean that a 200 amp service would satisfy this residence? I realize future growth might affect your answer, but even if you were satisfied to disregard future growth does that 200 amp service allow for the 198.83 of load. Maybe what I am asking is what exactly does that 198.83 amps represent? I know its not the same but if we had a 20 amp motor, we would not put it on a 20 amp breaker. thanks !
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
After running the Optional Calculation for One Family Dwelling,,, I come up with a diversified, bottom line number of 47,720 volt-amps ,, at 240V that divides out to 198.83 amp service. Does that mean that a 200 amp service would satisfy this residence? I realize future growth might affect your answer, but even if you were satisfied to disregard future growth does that 200 amp service allow for the 198.83 of load. Maybe what I am asking is what exactly does that 198.83 amps represent? I know its not the same but if we had a 20 amp motor, we would not put it on a 20 amp breaker. thanks !
Assuming your calc methods and math are correct, the 198.83 is 199 amp and a 200 amp service would be appropriate per Art. 220. Of course, as you mentioned, that does not allow for possible future needs.
 

smclott

Member
sorry,, my previous was supposed to be a new thread,,,,

sorry,, my previous was supposed to be a new thread,,,,

whoops
 
Status
Not open for further replies.
Top