If i do an upgrade using a meter/panel combo. I need to use 4 wire comming out of the panel into the panel in the house. 2 hots a neutral and a ground. I believe i am right just didn't know if there are exceptions to this.
thanks in advance
Chapter 2 Wiring and Protection
ARTICLE 250 Grounding and Bonding
II. System Grounding
250.24 Grounding Service-Supplied Alternating-Current Systems.
250.24(A)(5)
(5) Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non?current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.
Informational Note: See 250.30 for separately derived systems, 250.32 for connections at separate buildings or structures, and 250.142 for use of the grounded circuit conductor for grounding equipment.
Related Handbook commentary:
Section 250.24(A)(5) prohibits re-grounding of the grounded conductor on the load side of the service disconnecting means. This requirement correlates with the requirement of 250.142(B), which is a general prohibition on the use of the grounded conductor for grounding equipment. This requirement prevents parallel paths for neutral current on the load side of the service disconnecting means. Such parallel paths could include metal raceways, metal piping systems, metal ductwork, structural steel, and similar continuous metal paths that are not intended to be a normal current-carrying conductor.
250.24(B)
(B) Main Bonding Jumper. For a grounded system, an unspliced main bonding jumper shall be used to connect the equipment grounding conductor(s) and the service-disconnect enclosure to the grounded conductor within the enclosure for each service disconnect in accordance with 250.28.
Exception No. 1: Where more than one service disconnecting means is located in an assembly listed for use as service equipment, an unspliced main bonding jumper shall bond the grounded conductor(s) to the assembly enclosure.
Exception No. 2: Impedance grounded neutral systems shall be permitted to be connected as provided in 250.36 and 250.186.
(C) Grounded Conductor Brought to Service Equipment. Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be routed with the ungrounded conductors to each service disconnecting means and shall be connected to each disconnecting means grounded conductor(s) terminal or bus. A main bonding jumper shall connect the grounded conductor(s) to each service disconnecting means enclosure. The grounded conductor(s) shall be installed in accordance with 250.24(C)(1) through (C)(4).