I wanted to confirm my understandings of branch/feeder conductor protection for VFD's. When sizing a VFD feeder you must adhere to 430.122 and size the feeder conducotr at 125% of the VFD rated input current. 430.122 only specified required conductor size, and does not specifically adress any requirements to the upstream OCPD protecing this conductor. My understanding is that the upstream OCPD falls under the requirements of section 240 and must be sized to adequately protect the VFD feeder conductors.
I am curretnly working on a coordination study for several facilities where I notice that the OCPD feeding VFD feeder circuits are rated much higher than the conducotr rating of these feeders. For example in once case there is a 900A breaker which feeds (2) 4/0 of a VFD feeder circuit. These (2) 4/0 cables are only rated for 460A and are obviously not protected by the upstream 900A OCPD. I do not have the VFD nameplate info so I am assuming that the conductors are sized at 125% of VFD input per 430.122, and am just focusing on their protection by the upstream OCPD. I am looking at several cases where the feeder calbes do not appear protected by the upstream breaker.
Am I missing something in article 430 or elsewhere that allows for the breaker to be signifigantly larger than the conductors (similar to rule applied in 440.22 for compressors)? The only other thing I can think of is the design engineer is using the tap rule and basing the conductor size off of some main breaker or fuse located in the VFD's. I do not have access to the VFD's to verify these main fuses or breakers.
I'd appreciate any input on understanding this.
Thanks
I am curretnly working on a coordination study for several facilities where I notice that the OCPD feeding VFD feeder circuits are rated much higher than the conducotr rating of these feeders. For example in once case there is a 900A breaker which feeds (2) 4/0 of a VFD feeder circuit. These (2) 4/0 cables are only rated for 460A and are obviously not protected by the upstream 900A OCPD. I do not have the VFD nameplate info so I am assuming that the conductors are sized at 125% of VFD input per 430.122, and am just focusing on their protection by the upstream OCPD. I am looking at several cases where the feeder calbes do not appear protected by the upstream breaker.
Am I missing something in article 430 or elsewhere that allows for the breaker to be signifigantly larger than the conductors (similar to rule applied in 440.22 for compressors)? The only other thing I can think of is the design engineer is using the tap rule and basing the conductor size off of some main breaker or fuse located in the VFD's. I do not have access to the VFD's to verify these main fuses or breakers.
I'd appreciate any input on understanding this.