branch circuit feeders into main panel

Status
Not open for further replies.
I am installing a new service in a residential home. i do not like the look of all the nm going into multiple points of the panel. I would like to install a 2" pvc line and bring all the branch circuits into the conduit make a cleaner looking panel. I was trying to look up and code requirements on such a case?
 

iwire

Moderator
Staff member
Location
Massachusetts
I am installing a new service in a residential home. i do not like the look of all the nm going into multiple points of the panel. I would like to install a 2" pvc line and bring all the branch circuits into the conduit make a cleaner looking panel. I was trying to look up and code requirements on such a case?

That can only be done in some very specific circumstances and you might have to derate the cables if the conduit is longer than 24".

You have to meet each condition listed (a) through (g).



312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of
this article shall be protected from abrasion and shall comply
with 312.5(A) through (C).

(C) Cables. Where cable is used, each cable shall be secured
to the cabinet, cutout box, or meter socket enclosure.

Exception: Cables with entirely nonmetallic sheaths shall
be permitted to enter the top of a surface-mounted enclosure
through one or more nonflexible raceways not less
than 450 mm (18 in.) and not more than 3.0 m (10 ft) in
length, provided all of the following conditions are met:

(a) Each cable is fastened within 300 mm (12 in.),
measured along the sheath, of the outer end of the raceway.

(b) The raceway extends directly above the enclosure
and does not penetrate a structural ceiling.

(c) A fitting is provided on each end of the raceway to
protect the cable(s) from abrasion and the fittings remain
accessible after installation.

(d) The raceway is sealed or plugged at the outer end
using approved means so as to prevent access to the enclosure
through the raceway.

(e) The cable sheath is continuous through the raceway
and extends into the enclosure beyond the fitting not
less than 6 mm (1⁄4 in.).

(f) The raceway is fastened at its outer end and at
other points in accordance with the applicable article.

(g) Where installed as conduit or tubing, the allowable
cable fill does not exceed that permitted for complete conduit
or tubing systems by Table 1 of Chapter 9 of this Code
and all applicable notes thereto.
 