Are Seals Required for a Diesel Dispenser?

Status
Not open for further replies.

al

Senior Member
Location
Minnesota
Are seals required at the dispenser for a diesel dispenser even though it is not a classified location? See 514.9 Also, it appears that circuit disconnects are also required by 514.11 even though it is not classified.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Are seals required at the dispenser for a diesel dispenser even though it is not a classified location? See 514.9 Also, it appears that circuit disconnects are also required by 514.11 even though it is not classified.
Unless there is another motor fuel present, diesel does not usually create a classified location; however, you are correct, Sections 514.11 & 13 are still required, classified location or not, since diesel still falls within the Scope of Article 514. [Section 514.1]
 