I think what the answer is but...

Status
Not open for further replies.

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I am 90% sure that the answer is NO, but it is better to check with more experienced folks.

Would a whole house surge protector installed by the main panel, protect the electronics in the house against a utility lost neutral?

Thank you.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
TVSS

TVSS

I am 90% sure that the answer is NO, but it is better to check with more experienced folks.

Would a whole house surge protector installed by the main panel, protect the electronics in the house against a utility lost neutral?

Thank you.

Transient Voltage Surge Suppressors or more commonly now called Surge Protection Devices (SPD) react to voltage transients or spikes. They clip the upper portion of the voltage wave and absorb the energy that could damage sensitive SS devices.
So unless the open neutral causes the line voltage to rise above the surge threshold voltage, then the answer is no.
Also, it is important to note here that these SPDs work the best when installed closest to the equipment they are meant to protect (due to line impedance.)
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Whole House protectors are not sized nor built to accomodate lost or floating neutrals. Their voltage protection level is rarely below 300V, which is in excess of even full L-L voltage. Point of use surge protectors are often 150V so they would still be questionable in the case of a typical neutral problem.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
130414-1258 EDT

To be on the safe side the answer would be no.

Most of these transient limiters are some sort of soft knee varistor. Try to find a curve of voltage vs current for the one in which you are interested. Are these of value yes. Are there better ways possibly.

Many electronic circuits won't tolerate much over-voltage, and not for very long, possibly just milliseconds.

To really protect what is in a house takes many different things at the entry point, and distributed thru the house. At each important load point a back-to-back Zener diode pair (Transorb is one trade name) with a threshold somewhat above the maximum normal expected peak voltage would be useful, with some series impedance before the limiter. Zener diodes have a very sharp knee, MOVs do not.

Then do many things at the house entry bulkhead. Once there was a good discussion on the Internet about this by a radio amateur, but this disappeared a number of years ago. A large copper plate was the bulkhead, feed thru capacitors were in the bulkhead, a wide copper sheet ran from the bulkhead to the ground rod system (to reduce high frequency impedance), and various transient limiters. This provided very good lightning protection.

The bad neutral problem could be solved with shunt SCRs, Zener diode triggers, and fast blow fuses that the SCRs overloaded by a crowbar function.

Also you do not want additional grounding electrodes in the house.

To do a good job is not inexpensive.

.
 