Sajid khan
Senior Member
- Location
- Pakistan
According to NEC Reference 695.4 (B2) regarding the sizing of Fire pump circuit breaker we have to add the Lock rotor current of Fire pump and Jocky pump to get the size of breaker. My Question is, at the time of designing we do not know the code letter of Motor (code A to Code V Table 430.7(B) ) which correspond to the lock rotor current of the motor, so how could i calculate the lock rotor current of the motor and hence not the size of the main circuit breaker.
Is there any Rule of thumb or any other method of calculating the size of the main circuit breaker for the fire pump??
I have a 195kW fire pump motor whose code letter i donot know?? so what should be the size of main breaker??
Can any one Help Please...
Sajid Khan
Is there any Rule of thumb or any other method of calculating the size of the main circuit breaker for the fire pump??
I have a 195kW fire pump motor whose code letter i donot know?? so what should be the size of main breaker??
Can any one Help Please...
Sajid Khan