I have an existing Comm bldg. that has added a very small
office space to it, ...maybe 130-150 sq. ft. at the most.
Originally, the existing Comm. bldg. had 2 separate, exterior
GFCI rated receptacles, for an exterior application......The
new office space has enclosed the 2 GFCI rated receptacles
and added couple of more on to a 15 amp circuit.
I recently went to perform a Final inspection on the project,
and the EC has tied the existing GFCI rated receptacles,
...added 2 more and 2 separate fluorescent lighting fixtures
on to the one existing 15 amp. circuit.
I red tagged the installation for not having a separate lighting
circuit than the receptacle circuit......Now the EC is crying foul,
that it would cost him lots of money, time, blah, blah, blah to
go back and separate the 2 circuits......FWIW, I even asked
the EC directly if the NEC required that 2 circuits are required
for this application.....He acknowledged that it [ the NEC ] did
require 2 separate circuits......The bldg. owner called recently
and stated that they would remove 2 of the receptacles on the
15 amp. circuit and install a cover plate over the junction boxes.
My questions are: 1: What Articles require the separate
circuits?, ...2: Can this EC leave the install as is, with one OCPD
controlling the 2 lighting fixtures and the 4 receptacles?
As is the norm, ...this project has political attachments and they
will go over my head "Johnny Quick" if I cannot cite Article &
verse as to why the EC now has to go back to fix his mistake.
Any input is greatly appreciated!
: - :
I have an existing Comm bldg. that has added a very small
office space to it, ...maybe 130-150 sq. ft. at the most.
Originally, the existing Comm. bldg. had 2 separate, exterior
GFCI rated receptacles, for an exterior application......The
new office space has enclosed the 2 GFCI rated receptacles
and added couple of more on to a 15 amp circuit.
I recently went to perform a Final inspection on the project,
and the EC has tied the existing GFCI rated receptacles,
...added 2 more and 2 separate fluorescent lighting fixtures
on to the one existing 15 amp. circuit.
I red tagged the installation for not having a separate lighting
circuit than the receptacle circuit......Now the EC is crying foul,
that it would cost him lots of money, time, blah, blah, blah to
go back and separate the 2 circuits......FWIW, I even asked
the EC directly if the NEC required that 2 circuits are required
for this application.....He acknowledged that it [ the NEC ] did
require 2 separate circuits......The bldg. owner called recently
and stated that they would remove 2 of the receptacles on the
15 amp. circuit and install a cover plate over the junction boxes.
My questions are: 1: What Articles require the separate
circuits?, ...2: Can this EC leave the install as is, with one OCPD
controlling the 2 lighting fixtures and the 4 receptacles?
As is the norm, ...this project has political attachments and they
will go over my head "Johnny Quick" if I cannot cite Article &
verse as to why the EC now has to go back to fix his mistake.
Any input is greatly appreciated!
: - :