low-wattage
Member
- Location
- Pennsyltucky
Hello, first post here, apologies if this is under the wrong subforum or otherwise out of bounds.
I am installing datacom cabling for a new building with an automated lighting control system. The lighting control panels are network programmable. The network connections for the panels are located inside the lighting panel. There is no separation of any kind between the power and communications.
This of course gives me the heebie geebies since it goes against code and common sense to run class 2 wiring even in the same conduit or box without separation, let alone inside the panel. I assume there is some allowance for this - surely the panel manufacturer wouldn't create an unsafe product.
Two questions -
Can anyone cite the allowance / exception for this in the NEC? Is this considered remote control?
and,
Do I need to do anything different with my cabling? The electrician that installed the panel insists that just pulling this with the rest of my cable in that area, and running the cable into the panel and crimping a modular plug on it is acceptable.
I am installing datacom cabling for a new building with an automated lighting control system. The lighting control panels are network programmable. The network connections for the panels are located inside the lighting panel. There is no separation of any kind between the power and communications.
This of course gives me the heebie geebies since it goes against code and common sense to run class 2 wiring even in the same conduit or box without separation, let alone inside the panel. I assume there is some allowance for this - surely the panel manufacturer wouldn't create an unsafe product.
Two questions -
Can anyone cite the allowance / exception for this in the NEC? Is this considered remote control?
and,
Do I need to do anything different with my cabling? The electrician that installed the panel insists that just pulling this with the rest of my cable in that area, and running the cable into the panel and crimping a modular plug on it is acceptable.