i am installing lighting in a parking garage. using 6-bulb T8 fluorescent fixtures. whats the max amperage circuits i can use?
no freebies huh jumper?:lol:
read 210.23 (A), (B) and (C)
than read 505.4(B) jumper
read 210.23 (A), (B) and (C)
THats the article I had in question. the way interpret it, i can't use bigger circuits than 20. For 30. 40, and 50 amp circuits it says fixed lighting loads with heavy duty lampholders. i was wondering if i could run 30 amp circuits, and just tap off with # 14.
how does the #14 wire change a 30 amp circuit? If you don't have fixed lighting units with heavy duty lamp holders (non-residential), article 210.23 says you can't do it.
i thought i would be allowed to run #6s , and just tap off with # 14s, then there would be less wires going to the breaker panel, though that would only be allowed with heavy duty lamp holders, like those 400 watt metal halide.Not sure how long the runs are but can't OP come off a 50A +/- breaker at the MDP and put in a subpanel with 20A branch circuits to lessen the conduit, wire, etc.?