Customer has existing distribution panels connected downstream of a 30kVA UPS. The inverter output has an ungrounded neutral. There is a main distribution panel and subpanels from the main. Each panel is 120V with one leg (A) being line (hot) and the other leg (B) being neutral with no neutral bar in the panels. Thus, each circuit is fed by a two pole circuit breaker with one wire being hot and the other wire being neutral.
Can someone tell me why this was done? Is the neutral considered an ungrounded conductor such that it requires overcurrent protection? I have seen code references that all ungrounded conductors need to be simultaneously switched but I did not think the neutral was ever considered an "ungrounded conductor" rather an "ungrounded neutral." Is it something unique with UPS systems with floating neutrals?
Thank you for the feedback.
Can someone tell me why this was done? Is the neutral considered an ungrounded conductor such that it requires overcurrent protection? I have seen code references that all ungrounded conductors need to be simultaneously switched but I did not think the neutral was ever considered an "ungrounded conductor" rather an "ungrounded neutral." Is it something unique with UPS systems with floating neutrals?