I am hooking up a well for a customer and it has 12 awg coming out of the well head. I thought for some reason that wells had to be on a 30 amp minimum circuit. Am I wrong?
I am hooking up a well for a customer and it has 12 awg coming out of the well head. I thought for some reason that wells had to be on a 30 amp minimum circuit. Am I wrong?
I thought for some reason that wells had to be on a 30 amp minimum circuit. Am I wrong?
Yes. The circuit is sized to the motor.