I have been told that you cannot use SER to go from the 1st floor meter bank to feed the apartment panels on the third or fourth floor of an apartment structure. I cant seem to find a straight answer on this matter. It is an all wood, 4 floor, 54 unit building and the meter bank is on the first floor and the prints call for SER to each unit's load center panel. I keep reading that NM cable is permitted in level III, IV, and V construction, but i am not sure if NM applies to SER or not.
Please help... thanks.
[h=3]Service-Entrance Cable: Types SE and USE[/h] [h=4]I. General[/h]
338.1 Scope. This article covers the use, installation, and construction specifications of service-entrance cable.
338.2 Definitions.
Service-Entrance Cable. A single conductor or multiconductor assembly provided with or without an overall covering, primarily used for services, and of the following types:
Type SE. Service-entrance cable having a flame-retardant, moisture-resistant covering.
Type USE. Service-entrance cable, identified for underground use, having a moisture-resistant covering, but not required to have a flame-retardant covering.
[h=4]II. Installation[/h] 338.10 Uses Permitted.
(A) Service-Entrance Conductors. Service-entrance cable shall be permitted to be used as service-entrance conductors and shall be installed in accordance with 230.6, 230.7, and Parts II, III, and IV of Article 230.