Is it permissable to run instrument air lines in the same raceways as the signal wires?
Is it permissable to run instrument air lines in the same raceways as the signal wires?
300.8 Installation of Conductors with Other Systems. Raceways or cable trays containing electrical conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
Is it permissable to run instrument air lines in the same raceways as the signal wires?
725.3 Other Articles. Circuits and equipment shall comply
with the articles or sections listed in 725.3(A) through
(J). Only those sections of Article 300 referenced in this
article shall apply to Class 1, Class 2, and Class 3 circuits.
I do not see 300.8 referenced in 725 or 800.