MV solid state relay setting - guide?

Status
Not open for further replies.

anbm

Senior Member
Does anyone know any guides how to set the MV solid state relay?
Especially 50N,51N (neutral instantaneous and overcurrent). Thanks.
 

zog

Senior Member
Location
Charlotte, NC
You mean how to input the settings or how to determine the settings? They should be determined from a coordination study, when you use a basic guide for settings the end result is often what happened at the superbowl.
 

anbm

Senior Member
You mean how to input the settings or how to determine the settings? They should be determined from a coordination study, when you use a basic guide for settings the end result is often what happened at the superbowl.

Sorry...setting relay input (long time delay, instantaneous, etc) to archive the coordination study...
 

rcwilson

Senior Member
Location
Redmond, WA

We will need a lot more information. I'm guessing that SEL has a thousand different relays, and a couple hundred that might be able to do MV overcurrent protection.

This is a pretty broad subject. I have been doing it for only 40 years and still am baffled at times. I'm only saying that to emphasize the scope of the question you are asking.
 