300.22(C)(1)(2)Wiring in Ducts,Plenums,and other Air Handling Spaces NEC 2008

Status
Not open for further replies.

mjc1060

Senior Member
Hi,
I am working in the Chicagoland area(Rosemont) and does anyone know if the NEC requires gasketed luminaires & J-boxes also are there any additional requirements for communication cables.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The NEC does not require gasketed boxes in that application, but I believe the Chicago code and many of the suburbs do.
As far as the communication cables, if not in a metallic raceway the NEC will require "plenum" cables. It is likely that the local codes in that area will require metallic conduit for the communication cables.
 