Open Neutral
- Inside the Beltway
- Engineer
Thanks...just looked it up
There's a contemporaneous thread on same here...
See, that's where I am confused on the entire situation. It really isn't the POCO's business as it is on the customers side of the meter. You can run the feeders for a thousand feet if you want to IMO. Voltage drop is determined by the load, why does the POCO try to limit customer wiring if they aren't responsible for it? It reminds me of the post going now where the locate guy took the bond loose like an idiot. Hey, maybe this is the same guy...
My thoughts also, if this is not POCO owned wiring, why do they care?
I can understand not wanting to give them an easement, but unless it serves more than just your property is an easement necessary?
I personally would want the transformer closer than 500 feet most cases. Just adding one load sometime down the road can easily make voltage drop a problem even though capacity is otherwise there.
The problem with re-taping the primary for voltage drop is a motor load start up current will still cause dimming of lights, and as said it will also cause over voltage when the load is less which can shorten the life of lamps as well as electronics, I never suggest re-tapping or buck/boost for voltage drop problems, providing a higher voltage will only provide dimming lights at the higher voltage.
Here is a nifty VD calculator that will also give you the temperature the wire will run at if you want to play with the figures:
VD Calculator
Scroll down the page to get to the calculator
I re-measured the distance this weekend, and it's actually more like 400'. With my calculated load, overall voltage drop, including branch circuit drop, would be around 2% with aluminum 250s. That should give me plenty of room for additional loads.
I can't see why this wouldn't work since you have calculated for connected load. I realize you can't include diversity for the calculations but it is still there.
...and what if they say you should use 300's or 350's???I can't see how they could SAY no. :ashamed1:
Update on stubborn POCO...STILL stubborn POCO!! The manager agreed with my calculations and agreed that I should have no voltage drop issues with my proposed install. So what's the problem? They are still refusing me a variance by saying "That's just our policy...If we let you get away with it, we'll have to let other people get away with it...and we're not willing to do that." What a crock of sh..! They'll let you run 4/0s 250' but not 250s 370'. Why? Because they said so.
My next and final step is to plead my case to the Board of Trustees, and just hope that they'll listen to reason. What a nightmare! :rant:
So, the POCO says no conductors can be over 250 feet long after the meter base, correct? where are they measuring from? What if you have a well that is 400 feet deep, 100 feet from the house? Call the public utilities commission, see what they say. http://www.dps.ny.gov/
I still fail to see why anything beyond their delivery point is of any concern to them. Here it is not uncommon at all for field irrigation service conductors to be 1400 feet long or even longer. POCO stops at the disconnect they install directly below the meter which is usually at the road, the irrigation equipment is commonly 1/4 mile or so from that point in the center of the field.
You beat me to it, here in Indiana our Indiana utility commission would put a stop to this companies demand real quick if it is after the meter as I have posted many times on here.
It sounds like this utility is out to try to make as much money as they can off customers as well as to make right of ways for them if houses in the future are built next to this property, I have never ever had a utility with such an outrageous requirement, sorry we are allowed to spend our hard earned money they way we wish, if they are not footing the bill I can not see how they can demand how you install your conductors as long as it meets the code, it is your money being spent not theirs, and that is how I would approach it with the utility commission.
This would be like a gas station saying you can only buy gas if you own a vehicle that cost over $50,000 dollars, but at least with a gas station you have a choice to go to another, that is why we have utility commissions to keep them from doing this type of thing.
No one has the right to tell us how we must spend our money if the cost is ours to bare, as long as it meets code for safety.
I had a lineman and inspector who were cahoots with trying to make electricians to only install RMC for services, the inspector couldn't keep me from using PVC because we have state wide uniform codes, so he was able to get a lineman to try to tell me that his utility doesn't allow PVC for risers where the riser doesn't support the drop like on a gable end and is clearly allowed by code, one call to our state AHJ which he called the utility commission for me and had me tell them the city and inspector as well as the line man who was trying to enforce this for the inspector, well to make the story short, they both lost their jobs which wasn't my intent but now i have a city and linemen who respect me when they deal with my work, most city's and county's around here know me by name and only enforce to the code as it is written.
Wasn't long ago a member of this forum who had a problem with a local city here who was trying to make him drywall a garage or rewire the whole garage in pipe because he installed an electric car charging station that met the code using NM wiring methods, I made a call to our state ahj on his behalf who had the city remove the red tag and passed the job, one thing I have learned is that rouge inspectors are like children, once they learned that they wont get away with trying to enforce their own agenda, they learn to respect the rules or it will come back to bite them, give into them and you are at their mercy, if you live in a state that doesn't have state wide codes, then get involved with other contractors who are willing to fight, use the media to help promote equality through out the state and bring and end to the control that some inspectors think they have, your future customers will thank you for stopping requirements that many times are only enforced to make jobs cost much higher so the little man can't compete with the larger company's as in most of these requirements there is no added safety and if it meets code and the fact that a customer is allowed to spend their money the way they wish and as long as it meets the code that is their right.
Sorry for the rant, But over the years I have fought hard to stop this type of abuse and to protect not only my rights but the rights of my customers, and as above even helped a multitude of other contractors around here in doing the same who didn't know they do have a way to stop this abuse.
Maybe they are giving you a hard time because you are not from the area. It happens.I'm pretty confused myself. I've never done work in Vermont before and am used to dealing with the POCOs in my area of NY. I know people with 800' driveways who have 4/0s secondaries and have had no problems at all with voltage drop. POCO brought up the issue before connecting and made them sign a waiver releasing them from liability should voltage drop be a problem.