Power Factor verses Efficiency

Status
Not open for further replies.

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I can get IEEE 1459 Monday. I'm really curious why two new terms are defined that appear to be already well understood and well defined.
I was doing great until last week when someone had the audacity to call and offer money for time. Sigh ... Capitalism

However, I got a copy of IEEE1459 today. And a couple of hours to look at it.

Active power is not a new term. From IEEE 1459: ...
Yes, it is not new. And yes it is marginally different from average power.

As for the intrinsic term, it separately identifies the part of instantaneous power that is always present with oscillating systems.
Yes. That was clear from the context of the post where I questioned.

And I can see why I wouldn't have run into the nuiances before.
IEEE 1459 said:
e) There is a need to quantify correctly the distortions caused by the nonlinear and parametric
loads, and to apply a fair distribution of the financial burden required to maintain the quality of electric service.
The utility dollars never have rarely been a concern. Just the dollars for mittigation to keep the rest of the equipment functional/reliable.

There really weren't any new concepts. Mostly just arranging the models to provide standardizaton for billing instrument designs.

But I have seen it now. New math models are always interesting. So thank you.

ice
 