When calculating the 120% buss ampacity, does a 3 pole 60 amp breaker count as 60 or 180 amps toward the final calculation?
You are starting off with the reasonable assumption that the three pole breaker is mounted in a three phase panel with one pole on each phase bus. If this is not the case, then the answer changes.I knew the answer but I wanted some affirmation. I am designing my first system and I'm over thinking everything and second guessing myself. Thanks for the reply.
I knew the answer but I wanted some affirmation. I am designing my first system and I'm over thinking everything and second guessing myself. Thanks for the reply.