Kitchen small-appliance circuits

Status
Not open for further replies.

jeff48356

Senior Member
I know that the code requires two 20-amp small appliance circuits in the kitchen. But do these need to be on opposite legs in the breaker panel? I'm not talking about an MWBC, but simply two separate 12-2 feeds (one for each set of outlets).
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
Are you asking if they have to be on different phases? If so, the answer is no.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
But do these need to be on opposite legs in the breaker panel?

There should be an attempt to provide a balanced load across the legs. If that can best be done by putting the two SABCs on opposite legs, then it would be good design, but not a code requirement. If the best way to get overall balance is to put them on the same leg, great.
If it is just a question of making the wiring in the panel neater, that is OK too....
 