Im working on a small chain restaurant that has approximately 29 feet of show window and just want to make sure I have this all correct. I received a electrical code comment that says "Calculate show window load per 220.43". Im pretty familar with 220.43 but it seems excessive.
So basically 220.43 says 200 VA / ft * 29 feet = 5800 va * 1.25 (continuous) = 7,250 va. Lets say I put 1900 VA on a circuit, this would be 7250/1900 = 4 circuits.
210.62 says I need (1) receptacle within 18" of the window every 12 feet. 29 feet/12 = 3 receptacles. I cant put one receptacle on two circuits (without putting 208v in one box anyway) so I actually need to add one additional receptacle.
Is this all correct? Anyone agree that 7,250 watts is excessive for a show window? I need to actually add a whole panel to accommodate all these circuits.
So basically 220.43 says 200 VA / ft * 29 feet = 5800 va * 1.25 (continuous) = 7,250 va. Lets say I put 1900 VA on a circuit, this would be 7250/1900 = 4 circuits.
210.62 says I need (1) receptacle within 18" of the window every 12 feet. 29 feet/12 = 3 receptacles. I cant put one receptacle on two circuits (without putting 208v in one box anyway) so I actually need to add one additional receptacle.
Is this all correct? Anyone agree that 7,250 watts is excessive for a show window? I need to actually add a whole panel to accommodate all these circuits.