ptonsparky
Tom
- Occupation
- EC - retired
We are monitoring the current for Motor 1. Running, Max, and Minimum. We record the Max/Min after the motor has ran for 3 seconds.
Running is about 21 A with a no load condition. We have a broken belt minimum setting of 15 A which stops everything. Motor 2 starts when M1<22A for 15 seconds.
We were doing a final check out by moving grain today. Motor 2 had an auger that was frozen up which squealed some belts before we stopped it briefly and let it try to start again. The second attempt resulted in an alarm and shutdown caused by a "Broken Belt" alarm for current of 9 amps on M1.
We do not monitor M2, other than an N/O contact on the starter. The 4-20 ma cable for M1 is in a separate raceway from both motor feeders. We repeated the test with the same results then moved on to other issues. Could the LR of a small motor (7.5 to 10 hp, 3ph, 240v) result in enough VD to the power supply for the current transducer to cause this? We were not expecting this so had no VO
Ms connected.
Running is about 21 A with a no load condition. We have a broken belt minimum setting of 15 A which stops everything. Motor 2 starts when M1<22A for 15 seconds.
We were doing a final check out by moving grain today. Motor 2 had an auger that was frozen up which squealed some belts before we stopped it briefly and let it try to start again. The second attempt resulted in an alarm and shutdown caused by a "Broken Belt" alarm for current of 9 amps on M1.
We do not monitor M2, other than an N/O contact on the starter. The 4-20 ma cable for M1 is in a separate raceway from both motor feeders. We repeated the test with the same results then moved on to other issues. Could the LR of a small motor (7.5 to 10 hp, 3ph, 240v) result in enough VD to the power supply for the current transducer to cause this? We were not expecting this so had no VO
Ms connected.