I have a 480V system. The Unit substation is located in 1 building with a 2 parallel circuit breakers feeding another building that has an automatic transfer switch. In the building recieving the parallel feeds the contractor has not provided a means of disconnect for each circuit.
My question is this: Even if the system is all under 1 management are disconnects required somewhere in my new building? My interpretation if 225.32 is that even with an Exception met a disconnect is still required somewhere in the new structure, it just doesn't have to be right where the service comes in the building. The Contractor is stating that because the entire system is monitored by the client, Exception 1, the only disconnect means required would be the circuit breakers located in the other building on the Unit Substation. Which one of us is right?
My question is this: Even if the system is all under 1 management are disconnects required somewhere in my new building? My interpretation if 225.32 is that even with an Exception met a disconnect is still required somewhere in the new structure, it just doesn't have to be right where the service comes in the building. The Contractor is stating that because the entire system is monitored by the client, Exception 1, the only disconnect means required would be the circuit breakers located in the other building on the Unit Substation. Which one of us is right?