Hi.
I am working on replacing a dimmer board in a theater and adding a ton of new dimmer circuits in the process. Hundreds of dimmer circuits.
I haven't done this type of work before to speak of, at least not to this scale.
The existing system has several conduits with 20 to 30 dimmer circuits in each conduit, so 40 to 60 current carrying conductors. All #12 THHN/THWN. I asked the dimming equipment supplier about ampacity derating. He said he thought NEC Art. 520 had exceptions in it so we wouldn't have to go clear down to 35% per T 310-15(B)(2)(a).
I looked in 520 and see that there is an exception that allows any number of conductors as long as you don't exceed the fill requirement but don't see where the ampacity adjustment is addressed.
I do see that diversified loads, like what we have in this instance, have a different derating chart, Table B-310.11 located in Annex B.
The chances of having all the dimmer circuits at full load to any given batten or box is practically none.
Each light bar over the stage will have 22 to 36 circuits. Each bar fed with a big-a SO cord. Doesn't really make sense that I would have to run several conduits to the 36 circuit bar when they would all be terminated in the same box and feeding a 36 circuit SO cord.
Anyone here got experience with this?
I am working on replacing a dimmer board in a theater and adding a ton of new dimmer circuits in the process. Hundreds of dimmer circuits.
I haven't done this type of work before to speak of, at least not to this scale.
The existing system has several conduits with 20 to 30 dimmer circuits in each conduit, so 40 to 60 current carrying conductors. All #12 THHN/THWN. I asked the dimming equipment supplier about ampacity derating. He said he thought NEC Art. 520 had exceptions in it so we wouldn't have to go clear down to 35% per T 310-15(B)(2)(a).
I looked in 520 and see that there is an exception that allows any number of conductors as long as you don't exceed the fill requirement but don't see where the ampacity adjustment is addressed.
I do see that diversified loads, like what we have in this instance, have a different derating chart, Table B-310.11 located in Annex B.
The chances of having all the dimmer circuits at full load to any given batten or box is practically none.
Each light bar over the stage will have 22 to 36 circuits. Each bar fed with a big-a SO cord. Doesn't really make sense that I would have to run several conduits to the 36 circuit bar when they would all be terminated in the same box and feeding a 36 circuit SO cord.
Anyone here got experience with this?