Assuming you have sprinkler heads in the elevator shaft and machine/control room, you will need (5) relays:
1. primary level recall
2. alternate level recall
3. flashing fire hat
4. shunt trip
5. shunt trip power monitor
Items 1/2/3 will require a wire pair to interface to the elevator controls. The elevator tech. will land these on the elevator controls, then they'll need to be landed on the contacts of your addressable relay module. You'll need to map the appropriate detectors to the appropriate relay--review the matrix of operations on your approved prints and familiarize yourself with ASME A.17.1 and NFPA 72--they both have detailed sections explaining how initiating devices are to be mapped and the theory behind it. Phase 1 recall will turn on a "steady" fireman's hat from the elevator controls side when item 1 or 2 is activated--this is the case for most detectors. Phase 1 recall initiated from shaft or machine/control room smokes will initiate recall also, but need to activate item #3--this input activates a "flashing" fireman' hat.
Shunt trip is a slightly different operation. Item #4 relay will be mapped to shaft and machine/control room heat detectors. Your relay will control the power to the coil of the shunt trip breaker--an alarm condition will close your contacts and energize the coil. The coil power must be monitored by the FACP and initiate a supervisory condition--this is item #5 (NFPA72 2007/ 6.16.4.4).
As noted above, your relays need to be mounted within 3' of the device they are controlling--see NFPA 72 2007/ 6.16.2.2. Hope this simplified version helps.