Arlington Boxes

Status
Not open for further replies.

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I just installed 3 gang Arlington boxes in a friend's house. 1 gang power, isolated from 2 gang LV/data. These boxes look good. I also found a way to mount 1 in a 12x12x4 metal box for a surface mount application.

Try these if you have not already. Only down side I see is that the power box is really not large enough for more than 1 12-2 NM cable. 17.5 sq inch, legally allows 5 conductors plus device. But the box is not squared out, has a lot of inset where cable comes in. If you do them, try to set up a j box somewhere with only 1 NM per box, or set 1 up as end of line.

I need to call Arlington and suggest that they square out the box space. That should be easy enough to do.
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I called Arlington after posting this. Guy there was very friendly and thanked me for calling in with my feedback. He said they always seek feedback and appreciate hearing it, good or bad. I also told him Arlington was good about coming up with things we really need.
 