Both my NEC and NECHB say this:
450.3 (B) Transformers 600 Volts, Nominal, or Less. Overcurrent
protection shall be provided in accordance with
Table 450.3(B).
Exception: Where the transformer is installed as a motor
control circuit transformer in accordance with 430.72(C)(1)
through (C)(6).
I cannot find a 430.72(C)(6).:?
Senior moment or is it not there?