Service Factor & Temp Rise
George Stolz
Windsor, CO NEC: 2017
Service Manager
In the following graphic...
Since the temp rise is 40?C, and the service factor is 1.15, then I can use 125% overload protection per 430.32(A)(1).
If the service factor were 1.14 and the temp is 40?C, then I must use no greater than 115%.
If the service factor were 1.15 and the temp is 41?C, then I must use no greater than 115%.
Are all the above observations correct?
Smart $
Esteemed Member
Ohio
Yes... but I highly doubt you will ever run across the oddball ratings :D
Gregg Harris
Virginia
Electrical,HVAC, Technical Trainer
I do believe that it is either or that allows 125%
Smart $
Esteemed Member
Ohio
Ahh! I believe you have a point.
If service factor 1.15 or greater, up to 125%. The temperature rise doesn't matter.
If temperature rise 40?C or less, up to 125%. The service factor doesn't matter.
Smart $
Esteemed Member
Ohio
Well, which is it? :)
I ask because I originally thought it was "either" but we all got the question marked as wrong when we regarded it as such.