Art. 215.2 (A) (4). The 2011 Code states in the last sentence; Paragraph 310.15(B)(6) shall be permitted to be used for conductor size. The rule is for whether or not to count the grounding or bonding conductor not sizing feeders. Is this a mistake or a typo in the code ? I checked Art. 550.33(B) Feeder Capacity, it says (in part) shall be permitted to be sized in accordance with 310.15(B)(7) Would anyone familiar elaborate on it please.? R. Mendez:blink:
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A new 310.15(B)(2) was added in the 2011 code and that shifted the following section numbers up by one. That change in 310.15(B) was missed and 215.2(A)(4) was not updated. 215.2(A)(4) should cite 310.15(B)(7),
 